Key
Takeaways
1. Performance-Based Approach of Swedish Fire Safety Standards Enables Design Flexibility Without Compromising Safety
Axel Mossberg shared Sweden’s approach to fire safety regulations for buildings with single exit stairs, focusing on performance-based design. Swedish building codes allow deviations from standard recommendations if safety levels are maintained. For buildings up to 16 stories, single exit stairs are permitted with specific requirements, such as smoke vestibules and fire compartmentalization. For buildings taller than 16 stories, performance-based design is required, involving factors like smoke pressurization and sprinklers, which are not mandatory in residential buildings unless part of a customized design. An example of a single-exit stair building in Sweden is the Turning Torso, a 52-story residential building that employs performance-based fire safety measures. The fire safety strategy in Sweden balances smoke control, fire compartmentalization, and structural integrity, with high standards for fire resistance and non-combustible facades. The flexible, performance-based approach ensures high safety standards, even in taller buildings, offering both innovation and reliability in fire protection.
2. Revisiting Safety Regulations is Crucial to Preventing Human Tragedy
Karl Wallasch, a fire safety engineer in the UK, discussed the fire safety regulations for single-stair residential buildings, emphasizing the evolving approach following the Grenfell tragedy in 2017. UK building regulations focus on safety, including means of escape, preventing fire spread, and ensuring fire service access. While these regulations are performance-based, offering flexibility in design, the primary compliance route has been Approved Document B (ADB), which up until recently did not limit the height of single-stair buildings. However, after Grenfell, the UK government introduced significant changes. In 2023, the recommended height limit for single-stair residential buildings was reduced to 18 meters, with the updated guidelines set to take effect in 2026. This includes requirements for sprinklers in buildings over 11 meters and smoke ventilation systems. Another compliance route, the BS-9991 risk-based approach, now also recommends restricting single-stair buildings to 18 meters, with additional provisions for travel distance and evacuation of mobility-impaired individuals. These changes reflect a broader shift towards prioritizing fire safety and public confidence in residential building design, influenced by political and insurance sector pressures.
3. Single Egress Stair Design Can Create Efficient, Community-Focused Co-Living Spaces
Mike Mariano from Schemata Workshop presented his work on single stair design and co-living housing projects in Seattle. In the late 1970s, Seattle allowed buildings with up to four units per floor to use a single egress stair, a policy that evolved over time, now permitting up to five stories of residential occupancy with certain restrictions. Mike presented on Capitol Hill Urban Cohousing, a five-story building with a single egress stair and elevator, promoting efficient design with safety features like sprinklers and stair pressurization. The project promotes co-housing, a concept inspired by Denmark, with nine homes surrounding a central courtyard. This design fosters community interaction while providing privacy, with a focus on resilience through neighbourly connections. The building’s design features include compact, shared spaces and efficient circulation, with a planning approach that encourages semi-public areas. Mike emphasized how this design fosters community life, even in a small, high-density space, despite a tight construction budget.
4. SES Buildings With Enhanced Safety Features Can Match the Performance of Two-Exit Buildings
Morgan Tritthart of GHL Consultants presented on the Vancouver-based firm’s report on single exit stair (SES) building design for residential buildings up to six stories, focusing on recommendations within Canada’s National Building Code (2020 edition). The report aims to provide alternative solutions for SES buildings while addressing risks, performance, and safety requirements. Key recommendations include limiting occupant load, floor area, and travel distance, while incorporating sprinklers, fire alarms, and smoke protection measures. A jurisdictional scan of global codes was performed, comparing SES provisions in cities like Seattle and New York. The report emphasizes that SES buildings with enhanced safety features, such as sprinklers and smoke control, can perform as well as buildings with two exits. It also suggests several enhancements, including fire-resistant doors, wider stair landings, and smoke protection methods. The report concludes that SES buildings, with additional safety measures and a risk analysis, can offer comparable safety to two-exit buildings under Division B provisions of the building code.
5. Zoning and Building Code Reform Requires Collaboration From Multiple Stakeholders and Buy-In at the Municipal Level
Ian Mulder presented Edmonton’s “Point Access Block” guideline which was developed to promote single egress stair buildings in the city. The guideline aims to increase housing diversity, including lower-cost and infill housing, and offers an alternative solution strategy to current building codes. It provides a performance-based approach to developers and designers, with emphasis on safety, including stair pressurization and fire department involvement. The guideline is part of Edmonton’s broader zoning renewal effort to encourage new forms of development, particularly for citizen-led projects. It also includes design elements that showcase the potential for high-quality, diverse housing.
6. Optimizing Exit Stair Designs for Minimal Material Use, Durability, and Carbon Efficiency Can Significantly Reduce Both Carbon Emissions and Costs
Ryan Bruer from Ha/f Climate Design presented a life cycle assessment (LCA) study comparing different exit stair designs to evaluate their embodied carbon and cost implications. One of the key takeaways from the study is that durability plays a significant role in reducing carbon emissions. Materials like gypsum, which have a shorter lifespan, lead to higher replacement emissions, while more durable materials help lower the overall carbon impact. The study also emphasizes the importance of addressing upfront carbon emissions, which is more urgent than increasing carbon storage, particularly for projects with stringent requirements. Another major finding is that sufficiency, or using the minimal amount of material necessary to achieve the same results, is both cheaper and more sustainable. The wood stud designs, both two-hour and one-hour, were found to have the lowest carbon and cost impact, making them the most effective for low-carbon, cost-efficient design. The study highlights that reducing embodied carbon and cost in exit stairs involves careful material selection, balancing safety, durability, and efficiency.
Full Panel
Transcript
Note to readers: This video session was transcribed using auto-transcribing software. Questions or concerns with the transcription can be directed to citytalk@canurb.org with “transcription” in the subject line.
Single Stair Sessions Day 2 – The 2 Ss: Safety And Sustainability
March 19, 2025
Jennifer Barrett Hello everyone, good afternoon and thank you for coming. And thank you to those who attended our session yesterday, highlighting examples and pilot projects. My name is Jennifer Barrett, I’m the Managing Director at the Canadian Urban Institute and we’re excited to be hosting this session as part of the Design Innovation for Middle Housing Single Stair Sessions series with our colleagues at LGA Architectural Partners. Today’s session is part two in the three part series and we’ll focus specifically on safety and sustainability. with presentations from professionals across North America, including those from Sweden, the UK, the US, and Canada. Day three tomorrow will be a CUI CityTalk that will focus more broadly on the topic of housing innovation, how policy constraints impact where and how we build housing, and how regulations can either stifle or encourage innovation. I’d like to note that this Knowledge Mobilization event is supported by the Canada Mortgage and Housing Corporation as part of their Housing Supply Challenge Round Four, “Building for the Future” and funded by the government of Canada. I would also like to acknowledge that all of us on the call are coming today from hundreds of communities across Canada and abroad. Here at the Canadian Urban Institute, we acknowledge the diversity of Indigenous peoples, including First Nations, Inuit and Métis, who steward the places we call home, and reiterate our individual and collective responsibility to foster understanding, respect and appreciation for the traditional keepers of this land. I’m joining you today from Ottawa, Ontario, the unceded territory of the Algonquin and Anishinaabe people, and many of our staff work from our head office at CUI in Toronto, the home of Indigenous peoples covered by Treaty 13, including the Mississaugas of the Credit, the Anishinaabe, the Chippewa, the Haudenosaunee, and the Wendat peoples. We honour their enduring connection to keeping this land and commit to an ongoing process of truth and reconciliation. I would now like to turn it over to Conrad Speckert from LGA Architectural Partners to give a recap of yesterday’s session, which will be followed by presentations from our professionals. Thank you.
Conrad Speckert Thanks, Jennifer. So LGA is really excited to be here today. We’ve been working on this project for the last year and a half as part of the CMHC Supply Challenge. Yesterday was a focus on architectural aspects. Today’s focus will be on safety and sustainability of single stair building design. And so today we’re gonna hear from architects, fire engineers, and building code experts from Sweden, Canada, and the United Kingdom, and U.S. Axel Mossberg will talk a little bit about Sweden’s building code requirements for single stair design. Karl Wallasch is joining us from the U.K. to discuss regulatory reform following the Grenfell Tower disaster and subsequent code change there. Mike Mariano is an architect in Seattle. He will walk us through the Capitol Hill urban co-housing project where he lives and works in a five-story single stair building. We’ll then turn to the Canadian context and hear from GHL Consultants who have been working on a very detailed technical report on SES building design recommendations. We hear from Ian Mulder at the city of Edmonton who will present the point access block guide that the city had developed. And lastly, we’ll hear from Ryan Bruer of Half Climate Design, which will touch on some key considerations in terms of embodied carbon and construction type for exit stairs. But just to quickly recap for anyone who wasn’t around yesterday, you heard from LGA and three other architects as we presented pilot projects and prototypes for single stair housing across Canada. We looked at the cost benefit of single stair design with six prototypes for infill housing. This was in terms of floor area efficiency, construction costs, net operating income, and residual land value. And so there’s been a lot of changes recently to zoning regulations and planning policy across Canada to allow for more housing in existing neighbourhoods really as an alternative to suburban sprawl. However, this type of what we might call gentle density, buildings like multiplexes of up to four units or small apartment buildings of up to six stories, are challenging to build on small lots. And so the goal of single stair design is really threefold. Firstly, it is to make these missing middle and small mid-rise housing types easier to build. Two, it makes the development of smaller sites more viable. And that really leads to three, which is to enable small-scale, what we might call citizen developers, types of organisations without the large amounts of capital required for land assembly or to acquire larger properties. Just to quickly talk about the prescriptive code, the National Building Code under Section 3421 and 998 says that any floor area in a building of not more than two stories in height is permitted to be served by one exit with a total occupant load served of not more than 60. And so in other words, any multi-unit residential building except for a stacked townhouse, of more than two stories is required to have two separate exits. This diagram shows the maximum height for single stair multi-unit residential buildings in jurisdictions around the world. As we work our way down the drawing, you’ll see a clustering of countries around the six to eight story height range, which really corresponds to the height at which additional high-rise measures are required in the Canadian context. LGA and David Hein Engineering submitted two code change requests to the National Building Code to allow single egress for buildings of up to 3 and 6 stories in height. And it is our understanding that this is at least a priority topic for the 2025 to 2030 code cycle. Since the first edition of the National Building Code of Canada was written in 1941, the NBC has contained the prescriptive model code requirements for the design of buildings in Canada. And in 2005, the NBC was transitioned to what we call an objective-based code, which introduced the objectives and functional statements to really clarify what the goals are of the NBC’s prescriptor requirements and what they’re intended to achieve. And so this is one option of code compliance since acceptable solutions by default meet the intended objectives of the code. The other option is the use of alternative solutions which must achieve at least the same level of performance related to the objectives assigned to the associated provisions. I’ll just note as well that single-stair in Canada is not a new idea. In 1984, two architects wrote a research report for CMHC to document the differences in apartment building layout in terms of fire safety. In the 1990s, a very well-known architect wrote several or two papers on the challenge in building Main Street housing, particularly in terms the two-exit stair requirement and parking requirements. And then in 1996, the former assistant director of the Ontario Building Code had written a study proposing single stair changes to the Ontario building code. And so today, 40 years later, this technical issue is receiving a lot more attention given recent planning policy reforms. The United States revised their limit on single stair about 20 years ago in recognition, particularly of sprinkler system performance and reliability. And so it is, in many ways, long overdue to discuss alternative solutions to address this issue in Canada. Last year, the NFPA, the National Fire Protection Association, also held a symposium to discuss single exit stair and to hear from stakeholders, particularly in fire services, across North America. The report included a comparison of fire statistics between building types. And according to the NFPA data, single detached houses are statistically the most dangerous type of housing with a death rate of 25 persons per million. On the other hand, apartment buildings of three to six stories have a death that is 80% lower. And so I mention this because many parts of the building code make it very easy to build houses while adding many costs and complexities to the construction of small apartment buildings. And now, as Canadian cities look to change, land use policies, and zoning bylaws, we will inherently increase the fire safety of Canadians by providing more housing options that are in sprinklered and fire alarm buildings. We will also be decreasing our per capita carbon emissions by eliminating further suburban sprawl and urban boundary expansion. So with that, I’m going to turn it over to Axel Mossberg to talk a bit about a Swedish perspective.
Axel Mossberg Right, let’s see if I can share screen. Let’s go. There we go. There we go. Hello everyone. I’m Axel Mossberg and I’m very happy to be here and talk about the Swedish perspective on single exit stair solutions. I am, let’s see, I think you got my bio in the chat, but I am a fire safety consultant in Sweden who is also, I’m also the research director of Sweden’s largest fire safety consultant company. And I have a small research unit with three people currently where we do both research and design work. I did my PhD in elevator evacuation and evacuation of high-rise buildings and also other complex environments such as underground stations and so on. I’ve also been the project lead for the Swedish SFP best practice guidance for how to do performance-based designing complex buildings where high-rises buildings is one of those situations that we have in Sweden. And also I do some standardization work. But I’m here to talk about the Swedish building regulation and what we do in Sweden in terms of single exit solutions. And to just give a sort of framework is that we a performance-based building code in Sweden, so we have functional requirements, which are well, they describe the function, at least ideally, what the building should perform, and they are not allowed to be deviated from – you always have to fulfil the functional requirement. However, then you have a general recommendation, which is similar to a deem to safety solution pretty much. It’s a recommendation on how to fulfil the functional requirement, but you are allowed to deviate from it, As long as you fulfill at least the same safety level or the safety level of the performance-based code that we have. We also, something that might be good to know is that we have no general recommendation for buildings above 16th floor. So that’s once you get above 16 floors, you have to do performance- based design, which is why the Swedish arrow in Conrad’s picture was on 16 floors. that does not mean that you… can’t build single stair solutions higher than 16th floor. It’s just that we don’t, it’s not included in the building code. You have to do a performance based design, but there are a lot of buildings with more than 16 floors, which I’m gonna show you in a bit here. Also in general, it’s good to know that Swedish buildings are not very sprinklered. We have sprinklers in Sweden too, of course. But in general, especially for housing, it is not a very common solution to sprinkler and it’s not included in the code. It’s just, if you do a performance-based design that you would include sprinklers in housing. It’s required in hospitals and elderly housing, but it’s also a common system to put in as a performance-based measure pretty much. And single exit stairs solutions are allowed for, for housing or apartment buildings and also for office use. It’s not allowed for public use, but for this that I mentioned. So I’m just going to flip through sort of the standard cases here in Sweden. This is a two to three story building. Here we have a, you’re allowed to have one exit and it’s not, it doesn’t have to be fire compartmentized. This is just a regular house pretty much, or houses built together, and you’re allow to jump from your window up to five metres above the ground. So it’s a self-evacuation. Well, strategy pretty much. So the rescue service are not intended to be part of the evacuation strategy here. And for buildings that have a few more stories up to maximum eight stories, and also with windows that are below 23 metres above the ground, you can use ladder rescue as your alternative exit. So then you’re allowed to have a open stair, which is a stair you can you can see here on the, on the picture, an open stair without smoke vestibules or fire compartments in between. So you just have your apartment door, which doesn’t have to have a closer or anything. It’s just a regular door, and this can be open in up to eight stories. The load bearing system here is R60, which is a standard requirement in Sweden for these top buildings, and the doors are required to be smoke tight as they open up to the stair. So it’s the S200 means that it’s a smoke, that’s a smoke tightness requirement, pretty much. So that is up to eight stories or 23 metres above ground. If you go above that, if you have a building with up to 16 stories, which is, this is also an apartment building, you are allowed to have a single exit stairs if you do it as a TR2 stair as we call it in Sweden, or TR2 trappa in Swedish. Then the difference between a regular stair and a TR2 stair is that you have a smoke vestibule in between, so here is a fire compartment between the apartments and the stair. So if there’s a fire in one apartment and the door is open, you will only affect the apartment on that specific floor, the stair will still be protected, it will have a smoke lobby. Here we have a higher requirement on the load-bearing capacity. We still have the smoke tightness on the doors towards the stair, but you have a lower smoke-tightness requirement for the… apartment doors, which is the difference in these ones. Also the door heading to the stair here has to have a closer, but the other door does not have to have it closer on it, pretty much. For buildings above 16 stories, as I mentioned, we do not have a general recommendation or its performance based design, but based on experience, I can tell you that we have a lot of 16 plus stories, story buildings, apartment buildings with one single exit stairs, you then have to have a TR1 stair or TR1 trappa as we say in Swedish. The Tr-1 stair is pretty much a smoke lobby with a pressurization system of the stairwell. So you pressurize the stair and remove the exhaust air, often using the elevator shaft. You have to use performance-based design, as I mentioned. Just talking from experience has here, so this will be different for each project, but for up to about around 20 to 22 floors, it’s very common to do this without sprinklers. And the performance- based design will then compare the different stair solutions pretty much. And when you go above about 22 floors you generally put in sprinklers to make the risk analysis come together pretty much. It’s the same load bearing requirements. You still have the smoke tightness requirement on the doors to the stair. It has to be closer to the stairs. It’s also closers on the doors towards the smoke lobby in this case. But there’s no closer in the, on the doors towards the the separate smoke vestibules here. You can also put compartments heading just in directly into the first smoke vestibule here but then you would have a closer requirement and due to the Swedish uh what is availability or requirements that is a very uncommon solution. So usually you put a separate smoke vestibule just to get around the closer requirements. So you would, yeah, due to availability requirements. Also, I thought I’d give you a few examples. That was, I’ve mostly been talking about apartment buildings and we have our Sweden’s second largest or tallest building. It’s an apartment building called Turning Torso. It was built in 2005, and it was just passed by Karlatornet here in Gothenburg last year in tallness. It’s 52 stories, 190 metres high. It’s a residential building. It has spring floors and stuff. It is a PVD fire safety design, but it’s also a single stair building. And then I give you, this is another example on the right, it’s a Kista Science Tower, that is a office building in Sweden, which is 32 stories and 24 metres high. It is a office building, also a single stair building, also performance-based design, but it’s similar to, just to give an example on office buildings as well, I currently have a few projects which is ranging from 20 to 27 floors with mixed different, I mean some residential projects and office projects with this single-exit stair solutions building. So and also just a finishing note here is that the Swedish requirements for fire compartmentation is in general EI 60 it’s a 60 minutes standard fire resistance. Also it should be noted that the facade requirement is that they should be non-combustible at least for buildings with three or more floors. Or pass a national test which is called SP FIRE 105, which is a full-scale fire test. As you can see a picture of it here, you build pretty much three stories of your facade and then you can’t have a fire spread above the second window, pretty much, or below the second window. Generally, it should be noted also that we have a quite high level of quality in buildings, I would say, just looking when I’ve been around internationally, especially when we’re talking about tightness of buildings in Sweden. It’s a cold country, I guess Canada is the same, but we are quite good at tightness in our building, pretty much. So that was my short slides on the Swedish building code. If you have any questions you put them in or contact me, these are my contacts and now I’ll leave the word to Karl.
Karl Wallasch Thank you and welcome, everyone. I’m just sharing my slides. I hope you can see this all now. It’s a pleasure to be here. Thank you. Good morning, good afternoon, good evening. My name is Karl Wallasch. I’m German, as you might hear from my accent, but I’m a fire safety engineer and I’ve been working in the UK for nearly 20 years. So it’s my pleasure today to give you a single stair perspective for residential buildings from the UK and it was really interesting to hear from the previous presentations you will probably see some similarities but also some differences. So similar to Axel I will start with the UK legislation what do you need to consider if you design and build something in the UK. Well we’ve got two pieces of legislation one is the one we have to consider when we design and construct a building which is the building regulations. Then we have another piece of legislation that comes into play when the building is in use and occupied, obviously a much longer phase of the building. Today, we’ll only focus on design and construction stage, the building regulations. And when you’re a fire safety engineer, similar to other countries, there are a few areas you need to consider and the building regulations are telling us to focus on. Focuses in generally life safety. And what do you have to consider? The means of escape, how do we get people out, but also how do get fire brigades safely in? Then we need to consider the materials to prevent internal fire spread, structural resistance, but also external fire spread and access and facilities for the fire service. And what’s now so special about these building regulations? Well, similar to Sweden, they are functional in nature. So what does this mean? The building regulations won’t tell any designer how many stairs a building needs, or how many exits or how wide stairs need to be, et cetera. But they give us a functional performance that is expected the building will achieve. And because we’re talking about single-stairs today, I brought you just a text from a means of escape. So as a designer, you have to design and construct this building with appropriate provision to achieve an appropriate means of escape, allowing people to leave the building to a place of safety. “Appropriate,” wow. What does this mean? Can you imagine I would tell an architect just design it appropriately? You don’t need me. Well, that’s not really helpful. Our regulator knows this. So why we have to comply with the building regulations, there’s no nice to comply to them or not. No, you must comply with them. You must comply to the functional requirements. The regulator has given us different compliance routes, different guidance documents that we can apply. Deemed to satisfy, I think, were the words that Axel used. And the most standard rule to achieve compliance with the building regulations is considered to be the approved document B. B because it deals with fire safety. There are other approved documents that deal with other things designers have to consider. Today, we just focus on approved document B and it’s a standard document. We’ll talk about this in a bit more detail uh… when i started in 2006 for single stair residential, well, there was no limit. It was just giving us guidance how to design a single stair building, but it was not restricting the height. And there’s a second route, which we call risk-based approach. So this is using British standards and this is using a different way how to get to an answer. For example, if you want to establish the maximum travel distance in a building. This document would ask you questions about the users of the building. Who is there? Are they awake? Are they familiar? Are they sleeping? But it would also ask you things about the building, what’s the geometry? What’s my ceiling height? But then also what is the active and fire safety provisions you anticipate to be in the building? Detection. Yes. Okay. Detection allows you to increase the travel distance. Sprinklers. Yes. because sprinklers allow you then also to increase the travel distance. So it’s a package. It’s a measurement, a risk-based approach that you can choose to come to your answer. And again, in this document in particular BS-9991, we’ll have a look in a second. Up till autumn last year, there was no height restrictions for single-stair residential buildings. It was giving us guidance how to design single- stair residential buildings, but not restricting the height of those. Here in the UK, we’re really proud of this. We have a third route of approval. And Axel mentioned this again, it’s a performance-based design, purely application of fire engineering. We’ve got an entire British standard about this, how to apply safely fire or performance- based design for buildings. So it’s really important to understand that in the U.K., you must comply with the building regulations, but you’ve got different routes that you can choose. And now let’s look a bit in more detail about these different routes. I mentioned to you already that a proof document B was the standard guidance and when I came to the UK didn’t restrict the height of the building. Obviously we had in June 2017 the Grenfell tragedy and a single stair residential building 24 stories not sprinklered, had a fire and unfortunately over 70 people died. A shock, a really shock not just to fire engineers but to everyone in our society. And the question was brought up on the way in the years after: how do we actually deal with single stair buildings? Why do we have them? And the few things that I just want to highlight in this timeline is that suddenly the residential sprinklers were introduced from 30 metres high to 11 metres height. So they brought down recommendation for sprinklers for block of flats. there was the National Fire Chief Council and Association that brings the fire brigades together in December 2022 and they said well we believe here it’s our opinion that we should restrict residential buildings with a height of up to 18 metres or beyond 18 metres and in the same month our government released a consultation asking the industry should we consider a restriction of height for single-stair buildings and residential design. Should this be 30 metres? In London, London was quicker. London suddenly said a few months later, you can no longer build tall towers with a single stair over 30 metres. And there was, the industry was really confused. Finally, the government in 2023 and up to 2024 confirmed that it’s their wish to change the guidance, not the building regulations, they remain functional, but the guidance of Approved Document B. And instead of 30 metres, they recommended now a height restriction of 18 metres. This document is released, but it’s not in place yet. It will come into effect in September 2026. So where does this leave us in the industry? I mentioned to you already approved document B. Currently, we could still design single stair buildings without any height restriction because it just comes into effect and in about a year’s time. And we do have built already single-stair residential blocker flats, not just over 50 or 100 metres, we have them over 200 metres. I think one of the tallest is 240 metres. But of course, we know ADB is changing. The appetite of this is changing and no one, as I’m aware, is building single- stair buildings at the moment. And what will they look in the future? Single stair residential buildings will be up to 18 metres height. You can see in these diagrams, they restrict travel distance to seven and a half metres in a single direction. They expect the stair to be ventilated, the lobby in front of the stair to be ventilation, general compartmentation of 60 minutes between flats, and they expect sprinklers throughout if you’re over 11 metres, and they are based on a stay-put policy, which means only those in the flat where the fire occurs will ask to evacuate. That’s ADB, it’s changing. Now let’s look at the second route, the risk based approach BS-999. Because there was a version from 2015 and suddenly in November 2024 it was updated and suddenly everybody was surprised or not, but it did restrict with immediate effect pretty much from the end of November 2024 the use of single stair buildings and residential use over 18 metres. So there’s the recommendation to have two stairs now for taller buildings, but up to 18 metres you can still build with a single stair. And similar to the thinking in ADB, we’re looking at travel distance and dead ends of seven and a half metres. If you have sprinklers, you can double this up to 15, so a bit more flexibility. It looks at ventilation of the corridors. It looks a ventilation to the lobby in front of the stair. It’s based on sprinklers, stay-put. It also talks much more in detail about evacuation levels because it’s a huge discussion in the UK how we evacuate mobility impaired person. So you can see already slight difference in ADB and 9991, but we know the direction that is going. We now have or we’ll have a height restrictions in both these routes. And I just emphasize a bit on smoke ventilation because we think in three different ventilation systems. The stair needs a ventilation, often a vent on top that just opens and provides a way of natural air in. Then the lobby in front of the stair needs pretty much the same ventilation as the stair, a natural shaft. And then the corridors, which have direct access to the flat. And the corridors where we expect smoke in the first instance, spreading from the flat into the corridor, should either have natural ventilation, but taller buildings, we expect it should be mechanical or a pressurization system that we also have seen working in the Swedish slides where you create a positive pressure to prevent smoke spread into certain areas. And a key area of the single stair buildings will be or has always been the ground floor. How do we get people really out from the stai, ideally directly to the outside without letting them pass again through corridors or flats or other risk areas? So, we come to the summary. Here in the UK, we have 12 and a half thousand buildings, residential buildings that we call higher risk because they’re over 18 metres. They are built since the 60s. We have them and we do know quite a lot of them have a single stair and we do know that some are over 200 metres. But obviously, since Grenfell, really this topic has been widely discussed in our industry and has brought attention from all kinds stakeholders. Um, and people have started to wanting in a way, or responding to this public perception to restrict the single stair with a height and people were thinking about 30 metres, 18 metres. Some people said 10 stories for longer period. We had uncertainty and a way that’s now overcome. We do have this height restriction of 18 metres, but ladies and gentlemen I can’t even tell you why it’s 18 metres, there’s no scientific evidence or research supporting the 18 metres. And I doubt we will ever get this. We have just used 18 metres because it’s somewhere in our height system in the UK. And it’s interesting as a fire safety engineer, just maybe my last point is that this height restriction, and it was discussed, you know, everyone had really an opinion about this, but it came down to a political decision and really driven, interestingly, by insurers or funders. Because a lot of them had the thinking that they do not wish to build and invest for 50, 60 plus years in a building that might be seen as unsafe. So they were actually the first ones to introduce certain height criteria. And that’s it from the UK. I do thank you and I’ll pass on to the next presenter.
Mike Mariano Hi everyone, I’m Mike Mariano os Schemata Workshop. I’m an architect and developer and a resident of a project that we call Capitol Hill Urban Cohousing. Based in Seattle, we have a small practice on the ground floor of the same building. An architecture studio of 16 people will do a wide variety of work, including housing, a lot of affordable housing for non-profit housing developers, a category we call “infra-tecture” related to transportation, mobility, and other opportunities for us. A brief history of the Seattle, the single egress stair in Seattle. In 1977, a building of any height, you know, with not more than four units per floor could actually have a single means of egress in the building, a single stair. That was ’77, in ’85 it was reduced from any height to six floors in height, you know, no more than four dwelling units per floor. And current code allows up to five stories of residential R2 occupancy, no more than for dwelling units per floor. We have some State legislation that came before our local agency last week and was passed, and will be enforced at the State level or available to everyone at the State level as of July, 2026. Our office has done a few single means of egress stairs, including this one, Sola, which has eight homes. The image on the right floor plan shows the single stair, the elevator opening onto it. This is for a developer that really wanted, you know, a high efficiency factor for each of the floor plans. So there’s no community area associated with that. It meets the intent of the code really at a bare minimum. There are other examples of single egress stair buildings in Seattle, spent some time on the land use and application of the one in the middle, which is a type three non-combustible material building. All three of these have very compact vertical circulation in them. So stairs and elevators that are really super efficient, which was interesting, you know, but I also found like that there was tremendous opportunity to capture that and make it more of a common area. So what I’m going to talk about for the remainder of my few minutes is a project we call Capitol Hill urban co-housing. So approximately located where the red circle is on this image, you can see the Seattle skyline in the distance we’re walking this is the city centre. The Capitol Hill neighbourhood was in the news internationally a few years ago for the Capitol Hill occupied protest zone, which is essentially just to the left of the red circle. So this ground zero for protests occurring in the East precinct, which was just on the left-of-the-image here. We have light rail station just to right of the park on the image as well. An aerial view of our project. So this is essentially a five-story building. We are similar to the one on the left, so I actually have to say that we’re the yellow and light grey one on right. So the one of the left was built a couple of years prior to ours under the exact same zoning restrictions for height setbacks off the power lines, similar really tight construction budget, tight construction cost budget that we were trying to hit. So they ended up looking kind of similar but there’s actually 32 units in the building on the left. Four stair towers, no elevator, and four units, up to four units per floor. Our building, the one on the right, is nine homes surrounding a courtyard space and a single-egress stair and elevator. On that single egress stair and elevators in the image on the left here, so you can see some of the safety measures that are visible here, but we do have a full FPA 13 sprinkler system throughout the building, fire alarm system, smoke detection. You can see the damper at the top of the elevator hoist way we actually save some money by not taking the elevator all the way up to this upper roof level, but there is a smoke and fire damper for a naturally ventilated elevator hoist way there. There is a stair pressurization fan just on the upper right here that you can see that actually pressurizes the stairs. So each of those egress balconies provides access to anywhere from one to three units per floor, no greater than a six metre distance from the front door to that doorway. Beyond the building, so, you know, the single egress stair in our case allowed us to do, you know, an economical building that we could get nine families together and develop on our own. So, this idea of co-housing is something that originated in Denmark and was brought to the U.S. somewhat recently, a few decades ago, but this idea of kind of living in a community intentionally and knowing your neighbours, we actually got this group together before we had a building. There’s a deep focus on community and privacy, the ability to kind of live together, but have your own home. So you can walk out your door and find a community and activity, but being able to retreat to your home as you would anywhere else. I call it a very comprehensive approach to resilience, the idea of knowing your neighbours and that those are the most resilient communities that we can build. A section through the building, so…our primary street is on the left here, 12th Avenue, there’s an alley on the right. The site actually sloped about a story up to the right, so we carved this courtyard out of the building, that stairwell, single egress stair, and the elevator is directly off of that. We’ve got two units per floor on the left for a total of six. We got what we call the common house, so a large community room with the highest occupant load directly off the alley, which allows egress up to that on the courtyard. There’s three units stacked above here. My home is actually one right in the middle here with the balcony. We have our architecture studio for a Schemata Workshop of 16 people down in the ground level. That single egress stair and the elevator and those balconies open to a very compact courtyard space that’s about 5.5 metres by 6 metres in distance. The balconies add a little more space to that. But it’s essentially what we call kind of the heart and soul of the community. So all the homes are whatever you can think of might be a home, but it’s that common area and circulation space, you know, in the diagram in the middle, we’ve drawn it yellow, so it’s that common area that connects us all together socially. So activities that take place around that courtyard space and that single egress stair. Typical floor plan here two units on the left in yellow is the elevator and the stair in the egress balcony, you know again, no more than you know, six metres of distance from one of the unit entry doors to the stairwell door. Yeah doors are rated on closers, stairs pressurized, the balcony is open…Um, we used a planning approach that we came across in, in Denmark too, that essentially created kind of semi-public areas of the home at that front door and kind of going deeper into the building for more private areas. An example of one of those homes looking East, away from that courtyard space and out to the private balcony in the home, you know, looking the other direction towards that courtyard space. For those who have seen Ted Talk that my partner gave on living in community, this is one of the still images from that. Spencer is actually in his window, you about a six metre distance, you from where I stand. The image on the right shows our front door. And those egress balconies, the elevator and the stairs are right over there as well. One of the advantages of that open space, I can open my front door and periodically come across activity occurring out in that space. So rather than a double-loaded corridor and multiple stairs serving a distributed kind of social function throughout the building, we’ve concentrated all of this activity into a fairly, you know, dense little space, you know that allows access to that stair and the elevator overlooking that courtyard space. The courtyard is in the foreground, the elevator is off to the right here, those egress balconies you can see. We’ve got a rooftop farm up there that looks out to the west. The occupant load up here was designed to be about 10, so the beds actually consume a fair amount of that space specifically to keep the occupant load down. I’m looking down into that courtyard, you know, throughout the year, there’s a tremendous amount of activity that takes place. So again, that concentration that’s allowed by having that single egress stare and the concentration of activity in the community. You know, my partner and I are constantly taking photos down because it’s just kind of this interesting reminder of liveliness of community and living intentionally there. Something came up yesterday and a lot of conversation was the ability to provide bike maintenance rooms in the building. Middle image here on the top is me kind of rationalising the investment that I’ve made in a lot of bicycle tools and make this equipment and offering a two times a year bike tune-up day for the community. Again kind of you know this multi-purpose space kind of at the heart and soul of the community serving a variety of functions celebrations you know watching the weather kind of between and outside the homes. So that’s, you know, an overview of kind of looking at, you know, what a compact building, you know, developed intentionally for a community can look like. It’s just one example, you know, we had a tight construction budget. There were a lot of constraints that we were dealing with, but we’re excited about the outcome. Thank you again to Conrad and everyone who put on this conversation today, and I’m looking forward to questions. I’m going to hand it off to Morgan next.
Morgan Tritthart Hello, everyone. Just getting everything shared here. All right. Um, so, my firm here, I’m GHL Consultants, we wrote a report on single exit stair building design in the Canadian context. I’m gonna run through the high level overview of it. Let me just get that out of the way here. Okay, so GHL, who are we? We’re a firm of engineers, architects, and technologists founded in 1992. We’re based out of Vancouver, BC. So we’re a building code consulting firm, first and foremost. So we help engineers, architects, and developers in interpreting and applying the building code. That includes alternative solutions. So if you haven’t actually heard of us, you probably felt our effects throughout the Canadian building industry. We were an advisory consultant on the six-story wood frame code change and Tallwood House at UBC is one of our… major milestone projects, the 18-story mass timber building. So our report was written for Round Four of the CMHC Housing Supply Challenge. In it, we provide recommendations for residential buildings up to six stories in building height that are served by a single exit stair. And we make recommendations in both part three and part nine of the code. We go a lot more in depth into part three, then part nine. So this report is a public document. I believe it has been published now. The intention is that this report is used as a resource for professionals to develop alternative solutions for single exit stair buildings in Canada. Apologies. So the background for this report was developed in response to the rising discussion around the topic of single exit stair buildings in Canada. We saw a lot of these early conversations around code changes, especially in BC. We definitely felt a lot of it happening and happening very quickly. And I thought that we could add some valuable discussion to the topic as a whole. The report is based entirely in the national building code (2020 edition). We’ve prepared it completely independently of the BCBC 2024 code change. We did that just so we could completely take it as a separate sort of endeavour. We ended up coming to many of the same conclusions, although there were some provisions that we ended up disagreeing on in the BCBC 2024 code change. So the report is generally structured in this way. So we have to define the problem, then we take a jurisdictional scan of SES building design from different building codes around the world. We do an egress analysis of prototype SES buildings that, those prototype buildings were created by LGA. We do a retrospective analysis of the NBC to give some sort of context between an older version of the National Building Code and the modern version of the National building code in order to show how much better buildings are now compared to when they were in 1980. Sprinkler reliability and fire data, we’d have a short discussion on that. And then we add some discussion around smoke protection measures of a single exit stair. So with the National Building Code, first thing you have to do with anything in the building code, you have read what it says. So what this whole thing is based around is sentence 3421, which prescribes two exit stairs. But it says sentences 2 to 4 are when you’re allowed to have a single exit stair condition in Canada. So sentences 2 to 4 are very important for when you’re writing any sort of alternative solution to this, because they will shape the discussion around the thought process of the NBC when it permits the inclusion of a single exit stair condition within a building. So what it does, it… You have to consider the level of risk in the acceptable solutions and what…how they’re mitigated and what is considered to be acceptable for when the building code allows you to have a single exit stair condition. And those answers lie within the intent statements of sentences 2 to 4, which says: limit the floor area, limit the occupant load, limit the travel distance, make sure that when you’re discharging, you’re not discharging, you know, one story up of the building. uh… and that there’s occupant familiarity. So, with the building code it says either you meet the acceptable solution or you can produce an alternative solution. An alternative solution is a solution that meets the minimum level of performance required by division B and areas defined by the objective and functional statements of the code. So the intent statements are there. They’re not required to be satisfied but they help colour discussion. So we thought it’d be very important to talk about the intent statements and we talk about them in the report. The objective and functional statements for sentence 34211, which is the sentence that you would be writing any alternative solution to, has four functional statements tied to three objective statements. I’m not going to go through all of them. But, to bring it back, it’s about the objective and functional statements attributed to the applicable acceptable solutions. So that just brings it all the way around to our opinion is that you can take the performance of a single exit stair building with additional measures and compare that to a two-exit stair building under Division B, and it would perform as well as that building. Next part of the report, we go into a discussion on risk and risk analyses. We’re recommending if you’re doing an alternative solution that some sort of risk analysis is provided, just to help quantify the level of performance of the solution that you’re proposing. Quality of data is really key. So acquiring that is, is I think paramount to any discussion around that. There are two guides in NFPA, 550 and 551, that could be helpful for this. We identified those two. It’s not the only way to do it, but it gives options here. 551 is likely the direction that I’ll be taking whenever I produce an alternative solution for this, it’s tough because the…it’s hard to do a fully quantitative analysis. You need a lot of data to do so. So you can do a semi quantitative analysis based on likelihood or consequence. And it allows you to control for variables and it allows to make a reasonable judgement at the end of it. Next in the report, we go through a jurisdictional scan across different building codes that permit the single exit stair condition in residential buildings. So there’s a lot around the world that do that, but we shortlisted it to seven different building codes: Seattle, New York City, England and Wales, Sweden, Finland, Australia, and New Zealand. So we took those building codes, analyzed them, broke the provisions down into four overarching categories for general building provisions: egress, exiting, fire separations and fire department provisions. From there, we break it more down into, you know, what construction type can you do? What’s the maximum building area? What’s maximum building height that you can do in a single exit stair building? Do you require sprinklers, fire alarm, all that stuff? And then from there, we take what we know in these other codes and then try and translate that to a Canadian context. Put that squarely within the building code that we use, and from there, try and make a reasonable assumption as to how can we, as well as we can, address the objective and functional statements related to the two exit stair requirements. So, um, bringing it back around, like I was saying, we’re looking for, what we have to do is try and limit the occupant load, limit the maximum floor area, limit the max travel distance, make sure that the exterior discharge is basically at ground level, and occupant familiarity. So for something like occupant loads, when we did an analysis, we would take the division B solution of a six story wood frame building with two exits. There’s no limit to the amount of dwelling units that you can have on there. You’re limited by the exit capacity of the two stairs. And it’s generally about 275 people. So that means you have 1,375 potential cumulative occupant load all the way down to level one where it discharges out. Our suggested limits for single exit stair buildings is a maximum of six dwelling units per story, an occupant load of 30 persons. And that would mean it’s 150 person cumulative occupant load on the five upper stories and maximum of 20 dwelling units served by the single exit stare.
Conrad Speckert Hi, Morgan. Just going to ask if you can move really quickly through the rest of our slides, because we have two more presentations to get through. So what we can also do is have a follow-up session to go in this in more detail. So really just one sentence for each one, and then we can get time for the last two presentations.
Morgan Tritthart Yeah, you bet. Okay, so we do the same thing for travel distance. We do a comparison between the division B scenario and make a recommendation for the single exit stair building design. In the end, at the end of that section, we collate everything into a general recommendations all the way through of each overarching section and each subsection. We do a part nine analysis where we do a comparative analysis between division B and the SES building. It’s based on the part three analysis. It’s nowhere near as in depth, but essentially you’re sprinklering the building and it makes it that much safer. So we go through an egress analysis using Conrad’s or LGA’s prototype design buildings. Use the SFPE guide for human behaviour and fire. The analysis, essentially, it’s as you would think it would be. You have less people, less density. Less density means quicker egress time. Um, we go through a retrospective analysis of the BCBC or the NBC provisions. Uh, we set it at NBC 1980, um, versus the, uh, modern NBC, um and compare the level of performance. Again, we were expecting that, we found that, you know, modern NBC would outperform the NBC 1980. So, we think this is important because there are design innovations that were, became acceptable solutions, but were initially based on an alternative solution approach. Which is, one of these things, one of these things are the introduction of the six story wood frame building that used to be an alternative solution, now it’s code. We go through a sprinkler reliability analysis and we use the NFPA report US experience with sprinklers, its fire data… Long and short of it is sprinklers and fire alarms in your building and your death rate goes way down. Same thing with the BC Office of the Fire Commissioner annual report: sprinkler your building, fire alarm, deaths go way down. There are limits with fire data and we talk about that. It’s related to outcomes, you can only, the outcome is only injury or death and there’s no discussion on if fire prevented the occupants from leaving…doesn’t stratify by year of construction, the standard of sprinkler. So we talk quickly in the report about smoke control in the single-exit stair context. We don’t prescribe smoke control in non-high-rise buildings, just because we expect the evacuation time to be low enough that smoke development will not affect that. However, we do think that some sort of smoke protection of a single-exit stair should be provided. And we came up with four potential means: exterior passageway which accesses the stair; a vestibule between the single-exit stair and the public corridor; the smoke exhaust or extraction method; or just pressurizing the single-exit stair. So as a quick check, our opinion is that a six-story sprinkler single- exit building is much safer from a fire and life safety perspective than a three-story unsprinkled building with a public corridor and two exits that’s permitted to be designed through Division B. Or ofa 600 square metre, three story unsprinkled house also can be designed and constructed through Division B. So our conclusion at the end of the report is we believe that the performance of one exit stair plus some enhancements can perform as well as the performance of two exit stairs plus the regular Division B provisions. And we do that through limiting occupant load, limiting maximum floor area, limiting maximum travel distance, exit discharging to grade, and the dwelling units have an inherent level of assumed occupant familiarity with the building. Other things that we would do to enhance NFPA 13 sprinkler standard regardless of building height: smoke detectors in lieu of smoke alarms in dwelling units – that’s a direct code compliant provision, but it allows it to be fire alarm devices, so you can see them on the panel; no 20 minute doors, so you have to have 45 minute FPR doors, requiring two layer construction at combustible floor assemblies and at the exit fire separations; increase of the stair landing width to 1500 millimetres for counter flow so if there are responding firefighters at the same time as people are evacuating, there is a place where there is counter flow; a smoke protection method, as I stated before, the single-exit stair would serve residential only, and it would be independent of any other exiting in the building; and on top of all that, to wrap it all up, it’d be a risk analysis. Alright, now I will hand it off to the next presenter.
Ian Mulder Thank you, Morgan.
Conrad Speckert Thanks, Morgan. Just to add, the report from GHL, I realized that went very quickly, is available online. And the link to it’s been posted in the chat.
Ian Mulder Okay, hello everyone. My name is Ian Mulder. I am an architect here at the, with the City of Edmonton and we’ve been working with LGA on the guideline that I’ll be presenting today. A couple things here, we call this the point access block guideline – I know there’s other terminology, single egress, maybe one day we’ll all come together on what the name is – but we’ve been calling it kind of both. We’ll look at a little bit of how this came to be in Edmonton and our particular alternative solution strategy and how that really works for the city itself and some of the unique qualities of the city and some the changes that we’ve made recently to zoning, especially with respect to infill and missing middle type housing. So a little background: in 2023, Councillor Michael Jans had invited Michael Eliason to come to the city and he did a couple of public presentations, one at the university and one for maybe more city staff and more inside staff requirements. And of course, Conrad Speckert was there as well presenting. And this really opened, I think, the eyes of both, uh you know, citizens and also the professionals here on the opportunities with with point access block type buildings. Which frankly I don’t think was on a lot of people’s radar at that time. Obviously it had been in Mr. Speckert’s mind for for quite a while as it was the basis of his thesis and obviously the continuing work that has led us here today. So thank you very much Conrad for being such a champion of this type. But that led to a lot of opportunity that we saw here in the city and we were all pretty pumped. Ultimately, we saw this as an opportunity to increase diversity of housing type. There was a lot of discussion on perhaps the opportunities for developers to create lower cost housing and that kind of thing. We’ll see how the market responds in time, but ultimately we see this really as a question of quality housing and more diversity. So Councillor Jans put together a motion which essentially directed the administration, including my group to start developing thoughts around this. And at the same time, of course, the CMHC Housing Supply Challenge was underway and that enabled us to get some funding to pursue this work. And the basis of our work of course was an alternative solution strategy and a general guideline. And I’ll speak a little bit more about what that guideline looks like and what the audience for it is, but ultimately we’ve taken the approach as has been alluded to by other folks here on the call of essentially respecting the current code. Providing the designers and owners with a basis for both understanding alternative solutions, because let’s be honest, not that many builders operating – especially in the residential world- use these as a common strategy. It tends to be more common in Canada, especially for commercial buildings and that kind of thing, but on small-scale residential, the hiring of specialty code consultants or fire protection engineers, you know to support projects is a bit rarer. So there’s an educational quality to our work. And we ended up hiring Dubb Architects, a well-known local firm here, who in turn hired LMDG co-consultants out of Calgary to do the technical analysis. And this led to the guideline that was released in the last month we call the Alternative Solutions Guide for Point Access Blocks. It’s linked here, you’re welcome to take a look at it, I believe this deck will be shared. It has five different subsections sort of designed for web use. Some background information, of course. Think keeping in mind that this is a guideline both for professionals, for citizens and for the development community writ large business people. So we’ve really tried to write it in a fashion that will speak to all of those folks and for the people that need to dig deeper into the more technical components of it, the information is there, but we’re not overwhelming people right off the bat. So the backbone, of course, of this work is the work that LMDG did, which is a technical report and an outlining of an alternative solution strategy, not an alternative solutions itself, because we’re not seeking to put in place a, let’s call it an AHA supported alternative solution that would work for all buildings, but essentially a guide for professionals. And the LMDG exemplar building that is described in their report asks a very important question. And that is what would cause a single stair to fail. And of course the analysis, which I won’t get into right now was certainly robust. You can read it in our report. They did a number of quantitative risk tree analyses, essentially demonstrating or reflecting upon how safe are current code-compliant two-stair buildings and relating those to a single-stair version. And it turns out the difference, statistically, quantitatively, is quite small. And so the guide is seeking to point developers and designers in the direction in which they may bring up that delta between the single stair and the two stair type building. And the focus of course ends up on the stair itself and there are different strategies that are outlined there including of course pressurization of stair vestibules and that kind of thing. We have stuck to a very performance-based strategy, so this is a little bit different than what GHL I think has indicated today. Again, we’re not seeking to hold the hand of designers or developers but to point in the right direction for AHJ acceptable type solutions. This goes back to the education piece. One of the elements here that’s really important to note too because of course there’s been a lot of conversation with Fire both locally and nationally and internationally on this change, let’s call it, to North American thinking around single egress stair buildings, is that we’ve also concurrently developed a guideline for the inclusion of the fire department in all, in the review of all alternative solutions. So this in a way took the pressure off of this particular issue, which is to say there had been a lot of focus on single stairs, but at the same time, this is possibly one issue of many that comes about regularly with respect to how alternative solutions are reviewed by the city. And so by the production of this guideline, we’ve been enabled to kind of chart a bit of a clear path for all parties, all interested parties within the city, who have a responsibility for keeping people safe, both from the code perspective and from the fire protection perspective. And finally, I’m going to get a little bit into what’s unique about Edmonton or what’s been going on in Edmonton. We’ve had a major zoning renewal effort underway for the last few years. And as of last year, we reduced the number of zones from 46 to 24 and diminished many of the exclusionary zoning practices. This is all in a bid to open up the city to new forms of development, particularly infill, and enable a lot more of that citizen-led development that Conrad spoke of at the very beginning. So part of our guide has the technical analysis, the support of the alternative solution strategy, but also this design element. And so you’ll see in the guide a review of common lot types within the city and the common zones they’re in. And a number of massing models relative to this single egress type that are available. Again, this is pointing the development community in the direction of what they could possibly do. Because let’s face it, these buildings in Canada, though the alternative solution strategy is available to anyone today and has been for a number years, it’s not a common approach. It’s risky for developers to hire. you know, those consultants to do that work. And it just simply hasn’t really been done very often. I think we have had, you know in the past 10 years, maybe three single egress buildings. It’s just simply not part of the mindset of developers. And we want to kind of showcase here what those opportunities are within the unique characteristics of Edmonton. So then we get into some of the design elements and again, showcasing how nice these buildings can be, the quality aspects. Really, I wanna shout out to Mike Mariano and his Capitol Hill Urban Co-Housing Project, quality-driven design, so often missing in the dialogue around the housing crisis and everything else that’s going on in this country, but producing good quality units for people with lots of diversity therein. And that’s really what we’re focused on here. So I won’t get into the details of some of these some options, but essentially. Dubb has created some quite interesting designs and showing how they work within the city. So in total, there’s the guideline. Happy to answer any questions and thank you to LGA, to Conrad and CMHC for supporting this work. So thank you.
Ryan Bruer Thanks Ian. I’m going to take it away here. Thanks to all the previous presenters. My name is Ryan Bruer, I’m co-founder of Half Climate Design and I have the pleasure of presenting our studies of, or results of our study on exit stair and enclosure construction types through a life cycle assessment. Quick intro to Half: three years ago, we started Half to answer the question “how do we half the embodied carbon of construction Canada this decade?” And so we’ve been doing this by partnering with policy makers and builders to to assess whole life carbon and cost on projects. So how heavy is an exit stair? The purpose of this report was to compare exit stair designs to understand how non-combustibility requirements as well as fire resistance rating could drive embodied carbon and costs through the selection of the system of the stair. So in the study, we compared six different designs of two-hour fire resistance ratings, and three additional designs with a one-hour FRR, all with equivalent frame sped ratings on the interiors for each of the designs. The baseline design was a code-compliant exit stair for a six-story residential building based on typical industry practise of construction and the material quantities were gathered based on this baseline. And just as a quick review of LCA of life cycle assessment, we know all construction materials come from somewhere, so what this study does, what an LCA is, is the process of quantifying the environmental impacts of those materials within a building from extraction all the way through until the building is no longer standing. So these were the results. They illustrate that an exit stair’s construction type significantly contributes to a building’s cost and carbon. And we’re gonna look at the results in a few different ways as we go here. First, I wanted to just go quickly through each of the types. Very quickly, you’ll see the design name, the fire resistance rating, the total embodied carbon, as well as the carbon storage through either carbonation or biogenic sequestration. List here, so this first design is the reinforced concrete at 36,591 kilograms of carbon dioxide equivalent. And that’s the standard for measuring global warming potential of greenhouse gases within a life cycle assessment. So that’s kind of metric you’ll see on each of these designs. If we go to the next design is the precast concrete design, there’s actually a 13% reduction in embodied carbon for this design. It’s based on a proprietary design from a local Ontario manufacturer. It achieves a thinner wall assembly. So less material means less carbon in this case. And likewise for the concrete masonry design, which was another 11% reduction in carbon. The steel stud design, marginal difference from the CMU, a 3% increase. And here, compared to the two-hour fire resistance rating, the one-hour fire resistance rating for the steel stud shows a 22% reduction in embodied carbon. And that’s entirely driven by the change in wall assembly from having two, two layers of type X gypsum on both sides of the wall to a single layer, and you’ll see this change for each of the one-hour systems assessed. So the wood stud here, the two-hour design, very similar to the previous, but in this case because we’re now using more wood products, there’s a more significant biogenic sequestration of carbon, so nearly one-third of the embodied carbon. And then again, when we go to the one-hour design, we see a dramatic reduction in body carbon. And then the final design is the mass timber, here showing the two-hour fire resistance rating design. And the mass-timber design was much more than the wood stud, much closer to the total carbon emissions of the CMU design. But because the volume of wood product in this system is… significant, you see the carbon storage, it likewise is much more significant. And then again for the one hour, you see that reduction with the reduction of gypsum used. So we’re going to go on to what we learned from this, and it’s really not about a choice or ranking between one or another. It’s about finding an optimal solution for safety, cost, and climate for any given project and site. So a quick review of what we’ve learned with three findings that I wanted to present today. The first was durability matters. Looking again, seeing the totals here shown by life cycle stage, I’ve highlighted in red the replacement stage emissions within each of the designs and you’ll see that some of them have considerably more porcelain than others and those are the designs that have more gypsum board than the others. So in this set of materials, the gypsium board had a 40-year service life and so in a way is a penalty on having less durable materials. This is something that, you know, looking into the design further, we would aim to reduce. Finding two was balancing carbon storage. Here we see the totals again, shown by element type, carbon emissions in grey on top and carbon storage in green below. Upfront carbon is the most urgent thing we need to address. So depending on the requirements of the project, it may be more important to address the grey upfront carbon rather than adding to green carbon storage below. And then finding three: sufficiency’s cheaper. And so we combined our life cycle assessment results with a cost estimate provided by Vermulans the costing consultant, and there was a pretty remarkable correlation between the two. I think the most important takeaway here is that every exit stair in a building has a significant cost and carbon implication no matter what the construction. But even within each of these types, there are changes we can make to reduce carbon and cost. Within the concrete designs, CMU was the lowest carbon and concrete carbon and cost option that feels right to us. Thinking what’s the highest and best use of a material in a building? It’s the question of sufficiency what’s the adequate amount of something to achieve the same results, right? That’s the goal we have where in this case less is less. And then this was also true for the lowest cost and carbon design where the wood stud in both the two hour and the one hour options were the lowest. So if you were looking to half your cost in carbon of an exit stair, this would be the one to choose. And then just thinking between these two wood systems, it’s, you know, for certain types and heights, should we really be using the same system? So thinking about, you know, at the different heights and different locations, whether it’s in Toronto or Vancouver. And so, yeah, I think just in conclusion, this does reflect some of the work we’ve been doing with government agencies and with professional associations to really raise the bar on best practices for low carbon building design. We use this kind of inverted pyramid of carbon mitigation strategies often. And I think you’ll see some of these designs and then the choice between two of them really hitting on a few of these points. So for all the details, please read the report, it’s on our website at halfclimatedesign.com. It’s also on the single stair website. And thank you for your time.
Conrad Speckert Thanks, Ryan. I realize we had a number of presentations today, and so that went a bit over time in terms of scheduling. We don’t have much time left for questions, but if everyone that’s interested wants to stick around for a few more minutes after 1:30, we can try to get through a few of them. And in particular I think given that we’ve had a number of presentations, some of them are more directed to various presenters. So the first question is a question to Axel Mossberg specifically, and anyone else is free to chime in as well. But in the Swedish context, and this question came from Jack Keyes, how do responding firefighters deal with occupants egressing at the same time as trying to access the fire floor in the Swedish context.
Axel Mossberg Yeah, so in a Swedish context, in a multi-story apartment building, we would have a defend in place strategy that is the general strategy in Sweden. Uh, so we would not accommodate for, uh, a counter flow in the stairs, stuff like that, but do we… For buildings above the 11 floors, we, we or 11 floors and above, it’s we do have a firefighter lift requirement and that would be the general access route then. But, but in general Swedish, the Swedish strategy is defend in place.
Conrad Speckert Then a question from Mark Showers to Karl Wallasch. In the UK, will the 18-metre height limit still be imposed if the performance-based approach B7974 is used, or is it only the two other paths, ADB and 9991, that impose this limit?
Karl Wallasch ] Yes, it’s a very good question. We don’t know. But in theory, if you can prove through engineering, through logic, if go back down to the fundamentals about fire, the chemistry, the physics, how people behave, respond, etc., you probably can. But unfortunately, the guidance, the standard guidance, the two different routes, the Proof Document B and the BS-9991 have now set out this recommendations. So in practice, I think it will be very, very difficult to prove that your design is in a way so much different from what the standard guidance recommends. And what I see in the industry already, people just have accepted now that we have a height restriction. So yeah, I don’t think people will use performance-based design unfortunately. I say this with a heavy heart because it’s obviously often the right thing to do.
Conrad Speckert Then a question from Brad Anderson about standpipes, and perhaps this can go to GHL. Standpipe requirements have not really been mentioned. Have you run into issues with only having one standpipe in one exit?
Morgan Tritthart Haven’t run into any issues with that, we would just suggest that follow what the building code says for standpipes, provide it as required and give the correct clearance around it.
Conrad Speckert Then another question actually from Brad to the Seattle context: is there a restriction on occupancies in the exit and particularly I guess referring to the balconies and community spaces, so that sort of exterior passageway condition, what sort of constraints did you face in the design of the exterior passageway.
Mike Mariano Um, I mean, slightly wider than the minimum required, um, you know, we haven’t had issues. I mean there is a lot of stuff out there, but we make an effort to keep the space clear. Um, and nothing, nothing else really came up specifically. It is an open balcony. So it was presumed that smoke would not gather at the underside of the access to the stairwell.
Conrad Speckert And then this is a question to, it was submitted during the Sweden presentation, so to Axel. Have there been any recent fires in the higher SES buildings to confirm theory with practical evacuation of occupants in the event of an emergency.
Axel Mossberg We have a, I mean, there are fires all the time and similarly to Karl, we have quite a large amount of single exits there buildings, so there is fires every now and then, unfortunately. But if we look at the statistics, we do have a, we do not see a significant, well, a few years back at least when I looked the last time, we do not see a difference, a big difference between taller buildings and low rise buildings. We similarly to the statistics you show have a vastly higher death rate in single houses and then apartment buildings are much safer but the height difference does not affect the risk at least statistically. Not that much.
Conrad Speckert Another question from Hamid here about, and maybe if anyone could weigh in on this one, between the number of units per floor, the number of dwelling units per floor, and the height of the building, which is more important to restrict for a single stair? Challenging question, but if you wanted to comment on the relationship perhaps between number of units and occupant load, and building height, and floor area, and travel distance.
Karl Wallasch I’m happy to say something from the UK’s point of view. It’s probably the height rather than the number of units because we restrict the length or the dimension horizontally of this single stair building anyway because we have travel distance restrictions on the dead end. So I think we will never be able because we need to achieve certain square metres or feet for people to live in. And I don’t think that we’ll have a high number of flats on one level and all wanting to think it’s there. It’s probably more the height in my view.
Axel Mossberg So just to give another perspective, then I would say, I would say that the big difference between a single stairs solution in Sweden and a multi-stair solution in Sweden would be the number of flats per floor. So generally, if you have two stairs, you would have more than double the number of apartments in that building, because then you have a much higher allowance for the travel distances. If you go in one way in the corridor, you’re only allowed to go 10 metres, but if you can go in two ways, you can have a 60 metre corridor. So when we look at doing our performance-based design with single-exit stair solutions, it’s quite easy if we have a reference building or a reference safety level with a two stair solution to say that at least if you’re looking at a single floor, the single-exit stair solution is probably going to be safer. Because if you smoke filled the corridor, you would still not be able to exit, even if you have two stairs, at least if you do a Swedish safety design. So in my view, that would be the number of apartments would affect the safety level more. But if you just compare a single stair to a single stair, I guess I would agree with Karl that the height is more important. But when comparing the different solutions, I would say the number of apartments is important.
Conrad Speckert Then another question from Laura here on buildings with additional mechanical systems will be more expensive. The question then relates that to water supply, but maybe I can simplify it a bit: to the various groups that have requirements for smoke control measures, be it mechanical or passive if anyone wants to comment or talk a bit about the cost and design and complexity of smoke control systems.
Mike Mariano I mean, at least in our experience with our project and the one I shared today, passive open ventilation of the balconies minimizes mechanical systems. We’ve got the stair pressurization fan, we’ve got a passive damper at the top of the elevator, and those need to be tested on an annual basis, but the equipment wasn’t really that significant and certainly a lot less than the cost that we pay for elevator maintenance contracts. As far as the volume of water for the additional sprinkler system throughout the building, I don’t know.
Conrad Speckert Um, I know we’re just about over time, so maybe I’ll just, uh, a chance if any, if everybody wants to say, uh, uh, put a brief one sentence, two sentence summary of their perspective on single-stair, their perspective on their own presentation. Uh, if there’s one takeaway, uh you’d like the people attending to, to bring away from the session. We’ll start with, uh Axel. No pressure.
Axel Mossberg That’s a tough one. But I think, I mean, I’m, of course, called by the Swedish legislation and the Swedish fire statistics and my point of view is a Swedish one. And in my, from my perspective, the single-exit stair solutions that I’ve designed and are involved with, I regard them as very safe buildings. And I think that the stair is of course a very important element, but I don’t think… I think -oh, my son just jumped in. I think there are other elements that might be more important.
Karl Wallasch Yeah, my view is that obviously I have worked for many years in a country where single-stair residential buildings were possible to any height. And I’ve seen if you design them right, holistically, robust, with all kinds of different measurements, I do believe they can be safe. And seeing now in the UK that we have this height restriction and they drop down, in my view, really low to 18 metres… and seeing what you are trying to achieve to raise the height and actually we are all about 6 stories, 18 metres that’s very similar. I think, I wish you luck because I think you’re on the right path and I really believe that you can come up with solutions to design them safely. We’ve seen great presentations, great solutions and I’m not worried about the height and the things that… you have in mind and I wish you all the best. Thank you.
Conrad Speckert And then we’ll go to Mike.
Mike Mariano I mean, at least with the project that I shared, and we didn’t set out to do anything groundbreaking. It was just using the single stair exception of the code to make an efficient building. So for an urban infill solution, at that scale, it worked really well for us. So, yeah, I’d love to see more projects at that scale. I encourage you all to do the same.
Morgan Tritthart Yeah, I think for us now, this is kind of where the rubber meets the road. We are now, we’re going into writing alternative solutions based on this now. So we’re hoping that it moves forward and we can get some positive change here. Unlock some more building typologies and, yeah.
Conrad Speckert I think that’s Ian next.
Ian Mulder Um, yeah, diversity of type and being aware as my presentation alluded to, of what, you know, what are the interests of the marketplace because fundamentally it’s those folks who are building and helping to support them. And bring that, you know,the knowledge from these kind of discussions through our professional associations and relationships with builders and others. I think it’s really important to make it as normal as it is in places like Sweden to have these kind of buildings. That’s kind of the remarkable thing to me is that, you know, we’re in many ways we’re twisting ourselves in pretzels and yet here they are living pretty meaningful and normal and safe lives over there. Obviously with differences in culture and firefighting and materials, but nevertheless… Anyway, hopefully in 10 years we’ll be talking about this like it was old news.
Conrad Speckert And then we’ll end with Ryan.
Ryan Bruer Yeah, I think the goal is to build high quality housing, building houses, not corridors and basements and parking. It’s about building housing that’s good for people and this, based on the work like the professionals here and others, seems like this is a clear pathway to get optimizing for cost and carbon and safety. So, yeah.
Conrad Speckert Well, I realize it’s been a long session, and compared to yesterday, which it’s easy for architects to talk about architecture, getting a room full of fire engineers and architects to captivate an audience for an hour and a half is a challenge in and of itself, but hope that the attendees enjoyed the presentations. And maybe I’ll turn it over to Jennifer to just do another plug for what’s happening tomorrow.
Jennifer Barrett Yeah, absolutely. Thank you, everyone. And thanks to those of you who are still with us, just encouraging you to sign up for the third session as part of the series, which is our CityTalk tomorrow at noon. You’ve registered through a separate link, which I believe has been posted in the chat and we look forward to seeing you all there tomorrow. Tomorrow’s conversation will be a higher level discussion with a variety of experts to talk really about how design innovation and regulations can help to in fact enforce and see greater housing diversity in our communities. Thank you very much.
Full Audience
Chatroom Transcript
Note to reader: Chat comments have been edited for ease of readability. The text has not been edited for spelling or grammar. For questions or concerns, please contact citytalk@canurb.org with “Chat Comments” in the subject line.
12:00:22 From Canadian Urban Institute to Everyone:
Welcome everyone! We invite you to say hello in the chat before we get started. Tell us what brought you here, and where you’re watching from!
12:00:37 From Canadian Urban Institute to Everyone:
Please make sure your chat settings are set to “Everyone” so that everyone can read your comments.
12:01:49 From Uli Egger to Everyone:
Good morning everyone
12:01:51 From Nicolas Lamoureux to Everyone:
Hello from Windsor, ON. Architect interested in any and all means for designing safe and affordable housing.
12:01:53 From Doug Robertson to Everyone:
Hi all! Logging in from Ottawa and looking forward to the discussion.
12:02:46 From Diana O’Donoghue to Everyone:
Hello from Edmonton, AB. Interested in incorporation of accessibility in affordable housing
12:03:13 From Marc Showers to Everyone:
Hello from Victoria BC! looking forward to the presentation.
12:03:16 From Canadian Urban Institute to Everyone:
We are recording today’s session and will share it online in the coming weeks. Subscribe to the CUI newsletter for updates: https://canurb.org/subscribe/
12:03:25 From dan schumacher to Everyone:
Hello from Waterloo ON CA
12:03:28 From Canadian Urban Institute to Everyone:
Please note that given the limited duration of these sessions, we are not able to answer to raised hands or questions in the chat. Do you have specific questions for the speakers? Post them in the Q&A citing what you are referencing (speaker, context, content), and we’ll try to answer as many as possible during the allotted time following the presentations.
12:03:28 From Joe Rogers to Everyone:
Hello from sunny Halifax
12:03:36 From Canadian Urban Institute to Everyone:
This knowledge mobilization event is supported by the Canada Mortgage and Housing Corporation (CMHC) Housing Supply Challenge – Round 4: Building for the Future, which supports innovative solutions that remove barriers to increasing housing supply in Canada.
12:04:02 From Canadian Urban Institute to Everyone:
We hope this session is as interactive as possible, so please feel free to share comments, references, or links in the chat.
12:04:04 From Pat Petrala to Everyone:
Greetings from unceded traditional territories of Semiahmoo First Nations & Coast Salish Peoples. See sun/moon rise & longest wooden Pier, tides, weather -storms & neat Seasonal lights & Plaza events. WhiteRockCity.CA
12:04:20 From Alina Perrault to Everyone:
Are we muted ?
12:04:38 From Alina Perrault to Everyone:
I just don’t want my audio to get in the way and cannot mute myself
12:05:03 From Canadian Urban Institute to Everyone:
All participants are muted, yes.
12:05:14 From Alina Perrault to Everyone:
Thank you
12:05:18 From Canadian Urban Institute to Everyone:
Welcome new joiners! Just a reminder to please change your chat settings to “Everyone” so we can all see your comments.
12:05:40 From Branislav Folic to Everyone:
Hello everyone, I am an internationally trained architect from Europe, currently based in Toronto.
12:05:47 From Canadian Urban Institute to Everyone:
We also have closed captioning enabled for today’s session. If you would like to turn it off, please click on the button at the bottom of your screen and disable.
12:06:42 From Canadian Urban Institute to Everyone:
Conrad Speckert
Project Manager, CMHC Housing Supply Challenge
LGA Architectural Partners
Toronto, ON
12:06:43 From Canadian Urban Institute to Everyone:
Conrad joined LGA Architectural Partners as a project manager for ReHousing the Yellowbelt, a research collaboration with the University of Toronto exploring ways to gently increase housing density in residential neighborhoods. He holds degrees from McGill University and the University of Waterloo and has worked with architects in Vancouver, Berlin, and Tokyo. Passionate about making housing more accessible, Conrad focuses on building code and zoning reform, with expertise in designing ‘missing middle’ and mid-rise residential buildings. He also shares his insights as a guest speaker at the Canadian Home Builders’ Association, discussing housing policy and smart growth solutions. He is currently the Project Manager for the CMHC Housing Supply Challenge.
12:11:46 From Canadian Urban Institute to Everyone:
Axel Mossberg
Research Director
Bengt Dahlgren Brand & Risk
Gothenburg, Sweden
12:11:48 From Canadian Urban Institute to Everyone:
Axel Mossberg is a senior fire safety consultant and the research director of one of the largest fire safety consultancies in Sweden. Axel holds a PhD in Fire Safety Engineering from Lund University, where he studied evacuation behaviour related to elevator evacuation. He has specialized in complex building projects and is one of the most experienced fire safety designers of high-rise buildings in Sweden. Axel is also an active expert in national and international fire safety design standardization.
12:17:16 From Canadian Urban Institute to Everyone:
Welcome new joiners! Just a reminder to please change your chat settings to “Everyone” so we can all see your comments.
12:17:29 From Canadian Urban Institute to Everyone:
Please use the Q&A function for any questions you would like the speakers to answer. Make sure to provide some context/name the speaker/presentation you want to address. Thank you!
12:23:27 From Canadian Urban Institute to Everyone:
Karl Wallasch
Director
Trigon Fire Safety
London, United Kingdom
12:23:28 From Canadian Urban Institute to Everyone:
A Chartered Engineer with more than 18 years of experience, Karl gained his qualifications in Civil and Structural Engineering at the Bauhaus University in Weimar, Germany. He has established himself as a respected fire safety professional by developing innovative fire safety solutions for new, existing, listed and heritage buildings. With a view to the future of the fire safety industry, he is also a tutor at the Bauhaus University in Weimar, Germany and currently a member of the SFPE Task Group for the Performance-Based Design Standards Making Committee. He served as the President of the Society of Fire Protection Engineers (SFPE) UK Chapter from 2018 to 2024 and regularly organizes international conferences for SFPE.
12:26:58 From Vina Hendra to Everyone:
Dr. Mossberg: Thank you, I have a couple of questions: 1. typical construction for residential homes: concrete or wood? 2. what air tightness level is required by your building code and what is typically achieved?
12:28:49 From Canadian Urban Institute to Vina Hendra, Hosts and panelists:
Hi Vina, please note that given the limited duration of these sessions, we are not able to answer to raised hands or questions in the chat. Do you have specific questions for the speakers? Post them in the Q&A citing what you are referencing (speaker, context, content), and we’ll try to answer as many as possible during the allotted time following the presentations.
12:35:34 From Blair Scorgie to Everyone:
18m is the height of a fire ladder…
12:36:45 From Canadian Urban Institute to Everyone:
Mike Mariano
Founding Partner
Schemata Workshop
Seattle, United States
12:36:47 From Canadian Urban Institute to Everyone:
Mike is an architect and a founding partner of Schemata Workshop, a Seattle-based architecture and urban design practice. His work focuses on enhancing the experience of living in and moving through the Cascadia region, recognizing that civic and personal well-being are deeply connected. He believes thoughtful design plays a crucial role in fostering social cohesion and community resilience. Mike is a past co-chair and current member of the Capitol Hill EcoDistrict Steering Committee, which recently earned certification as one of the first EcoDistricts in the nation under the imperatives of Equity, Resilience, and Climate Protection. He also chairs the AIA Seattle Committee on Adaptation & Resilience. Mike is a founder and developer of Capitol Hill Urban Cohousing, where he lives with his family and works in the street-level commercial space of a transit- and pedestrian-oriented community.
12:46:46 From Nicolas Lamoureux to Everyone:
Fantastic project.
12:46:50 From mario mammone to Everyone:
Great project Mike, love to see this concept in Montreal, Quebec!
12:46:51 From Ken Kunka to Everyone:
Hi, I have some questions in the Q&A. Having the occupant clutter in exterior passages is something fire departments get nervous about for post occupancy controls.
12:47:35 From Canadian Urban Institute to Everyone:
Morgan Tritthart
Architectural and Building Technologist
GHL Consultants Ltd
Vancouver, BC
12:47:36 From Canadian Urban Institute to Everyone:
Morgan Tritthart is an Architectural Technologist graduate from Red River College. With a passion for design and building, Morgan brings a deep understanding of Building Science and Building Codes to the GHL team. Over the past five years, he has honed his expertise in construction, surveying, and team leadership.
12:49:49 From Lauren Konken to Everyone:
For presenters part of Teams channels, going on do not disturb status during a call can present chat pop-ups on screenshares
12:53:19 From mario mammone to Everyone:
How do I see yesterdays re-run thanks again, also has anybody researched the Japanese designs. They seem to have these single stair low rise buildings.
12:54:25 From Canadian Urban Institute to Everyone:
All recordings for the Single Stair Sessions will be made available at https://citytalkcanada.ca/
12:54:26 From Canadian Urban Institute to Everyone:
Stay in the loop by subscribing to our newsletter: https://canurb.org/subscribe/
13:00:18 From Kathryn Dekraker to Hosts and panelists:
Question for Axel Mossberg: Are there post-construction, pre-occupancy testing procedures in Sweden for smoke-tightness and air-pressurization, or is there reliance on assemblies/details and engineer sign-off, without real-life performance testing? I’m listening from Nova Scotia, and having worked in construction as a carpenter, I’m not sure our labour skill/reliability is high enough for actual performance to be in-line with designed/calculated performance.
13:02:39 From Pavel Voronenko to Everyone:
Would the GHL report shared to the public?
13:02:56 From Marc Showers to Everyone:
https://ghl.ca/resources/single-exit-stair-building-design-supporting-documentation-and-recommendations/
13:03:21 From jim baxter to Everyone:
does smoke not develope before flame?
13:03:28 From Jennifer Barrett to Hosts and panelists:
In the chat: Would the GHL report shared to the public?
13:04:06 From Conrad Speckert to Everyone:
The GHL Report is available here – https://ghl.ca/resources/single-exit-stair-building-design-supporting-documentation-and-recommendations/
13:04:51 From Canadian Urban Institute to Everyone:
Presentation slides along with the recordings will be made available.
13:05:45 From Canadian Urban Institute to Everyone:
Ian Mulder
Project Architect, Facility Planning and Design
City of Edmonton
Edmonton, AB
13:05:46 From Canadian Urban Institute to Everyone:
Before finding architecture, Ian Mulder worked for many years as an artist producing murals, developing educational programs and working with communities throughout Canada and beyond. He later trained as an architect (M. Arch, University of Toronto) and helped design and manage a variety of commercial and institutional projects. Ian Mulder is currently an architect with the City of Edmonton’s facility planning group, and Chair of the Edmonton chapter of RAIC.
13:07:46 From Kathryn Dekraker to Hosts and panelists:
Michael Mariano – I saw Grace Kim’s TED talk about Capital Hill years ago, and she and your project inspired me to become a founding member of a cohousing project in Nova Scotia. It didn’t turn out quite as lovely (design-wise) as yours – but not bad for first-in-province! We went gallery access for egress with 2nd level outdoor walkways and outdoor stairs, and the whole project likely could have been much nicer and more affordable if the stair/egress code here was more in-line with Seattle’s and other places. I’m hoping we’ll see these regulations changed here soon – to the benefit of future cohousing and other projects
13:09:31 From Mike Mariano to Kathryn Dekraker, Hosts and panelists:
Great to hear – there’s many things that didn’t happen here as well as I’d liked either. The SES can help to make this scale of urban infill projects happen, but – as you know – there’s so much more to do that goes beyond just the building.
13:11:35 From Canadian Urban Institute to Everyone:
https://www.edmonton.ca/sites/default/files/public-files/Point-Access-Block-Alternative-Solution-Guide.pdf?cb=1741850063
13:16:14 From Canadian Urban Institute to Everyone:
Ryan Bruer
Co-founder
Ha/f Climate Design
Toronto, ON
13:16:21 From Canadian Urban Institute to Everyone:
Ryan is passionate about the communal stories that connect people to materials and city-building. A McMaster Fine Arts graduate, his work explored circularity, repair, and material exchange in Hamilton. At Ha/f Climate, Ryan has advanced life cycle assessment in architectural offices across Canada to drive immediate carbon reduction in the built environment. He leads the Ha/f Research Seminar at the University of Waterloo’s School of Architecture.
13:24:46 From Canadian Urban Institute to Everyone:
https://halfclimatedesign.com/research-policy
13:26:33 From Pat Petrala to Everyone:
Q Conrad & team – no answer urgent – next session response?
Have the Canadian Assoc. of Urban PLANNERs & Planning technicians see/discussed a briefing on the evolution of Single Stair options?
I trust Fire sector & Insurance folks at high level may be aware, yet how to get to front line?
What about LEGISLATIVE folks (e.g. BC MLA/ new Ministers & MP) & departments?
This topic would make an excellent series to have PUBC buy in, perhaps on Knowledge Network, CBC & all media.
13:27:43 From Canadian Urban Institute to Everyone:
Reports, research and prototypes discussed during Day 1 and 2 of the Single Stair Sessions can be accessed here: https://singlestair.ca/
13:27:59 From Ken Kunka to Everyone:
great presentations!
13:28:01 From Canadian Urban Institute to Everyone:
Thank you all for joining us today! If you have any questions you would like us to follow up on, please send them to cui@canurb.org
13:28:48 From Canadian Urban Institute to Everyone:
This knowledge mobilization event is supported by the Canada Mortgage and Housing Corporation (CMHC) Housing Supply Challenge – Round 4: Building for the Future, which supports innovative solutions that remove barriers to increasing housing supply in Canada.
13:29:10 From Canadian Urban Institute to Everyone:
Stay in the loop by subscribing to our newsletter: https://canurb.org/subscribe/
13:29:12 From Canadian Urban Institute to Everyone:
Follow us on LinkedIn and Instagram @canadianurbaninstitute and @lga_ap
13:29:22 From Yosh Imahori to Everyone:
Do other jurisdictions other than Sweden consider that defend-in-place is the required action for occupants?
13:30:21 From Zachary Mathurin to Everyone:
Thank you again for these presentations. Appreciate the construction and safety considerations and solutions. Looking forward to the final session tomorrow, cheers!
13:31:44 From Canadian Urban Institute to Everyone:
Single Stair Session resources and recordings will be made available at https://citytalkcanada.ca/
13:33:11 From Uli Egger to Everyone:
Thank you, very informative presentations today
13:34:10 From Hazel Battad to Everyone:
Big fan of Ian Mulder and his presentation. Thanks to all on the call!
13:34:26 From Zach Briguglio to Hosts and panelists:
Great presentations! I am curious how emergency services in North America (fire firefighters, etc) differ from European services in their responses to fire emergencies. Are they equipped to respond to fire emergencies the same way as our European counterparts?
13:35:28 From Tatiana Quintana to Everyone:
Thank you. Great Presentations.
13:35:51 From Philippe Beauparlant to Everyone:
Great presentation. Thank you
13:36:14 From dan schumacher to Everyone:
Great useful presentations Thank you
13:36:42 From Abdelkrim Habbouche to Everyone:
Thank you!
13:37:32 From Kathryn Dekraker to Everyone:
Thanks everyone – great presentations!
13:38:11 From Irteza Ahmed to Everyone:
Thanks everyone, really appreciate this.
13:38:58 From Branislav Folic to Everyone:
Thank you, great presentation and very important issue for the development of missing middle.
13:39:13 From inge roecker to Everyone:
Thank you everyone, very informative, Great work Ian Mulder and Edmonton
13:39:38 From Mary Kenny to Everyone:
Excellent information. So good to have people like this thinking, collectively, through the related issues and possibilities to address them.
13:39:49 From Lauren Konken to Everyone:
Thank you for the diverse views and perspectives! I learned a lot today.
13:39:50 From Canadian Urban Institute to Everyone:
Join us for Day 3 on March 20, 12-1:00pm ET CityTalk | Live
Addressing Canada’s Housing Supply: Can Regulations Drive Housing Innovation?
Register here: https://us06web.zoom.us/webinar/register/WN_F8jWnuiKT_mwrTgogTV8uQ#/registration
13:39:50 From Pat Petrala to Everyone:
FINLAND also has great examples. THANSK – will seek to make this option POPULAR with neighbours, builders and elected folks plus staff.
13:39:53 From Nicolas Lamoureux to Everyone:
Thank you all!
13:39:57 From Paul Walsh to Everyone:
Thanks so much for great presentations.
13:39:59 From Vina Hendra to Everyone:
thank you so much!
13:40:01 From Marc Showers to Everyone:
Great presentations. Thank you all.
13:40:01 From Crystal Waddell to Everyone:
It was fantastic. Thank you all
13:40:24 From Tristan Roberton to Everyone:
thanks everyone, very informative presentations!
13:40:30 From Conrad Speckert to Hosts and panelists:
Stick around afterwards if you have a few minutes!
13:40:33 From Omri Menashe to Everyone:
Great presentations today, very informative, looking forward to reading the reports!
13:40:33 From Canadian Urban Institute to Everyone:
Thank you all for joining us today! If you have any questions you would like us to follow up on, please send them to cui@canurb.org
13:40:35 From Mike Pospolita to Everyone:
Was interesting, thanks
13:40:38 From Allister Andrews to Everyone:
Thank you!
13:40:38 From Pat Petrala to Everyone:
13:40:40 From Sylvia Jennings to Everyone:
Thank you!